Old November 3rd, 2012   #1
outbackflyer
Junior Member
 
Join Date: Oct 2012
Posts: 3
Default New 10kW Generac standby not charging battery

I just finished installing my new 10k NG standby generator. Everything tests out but the battery doesn't seem to be charging. I removed the fuse and turned off the CB and installed a new battery and the unit starts, transfers and produces the expected AC supply. The battery over time and multiple starts becomes dead. I can charge the battery with my battery charger and re-install and the unit is happy until the battery runs down again. Is there something I can check or can I assume the controller is bad?
outbackflyer is offline   Reply With Quote
Old November 3rd, 2012   #2
HKFever
Senior Member
 
Join Date: Sep 2011
Location: Chesterfield VA
Posts: 610
Default

Did you hook up the "T1" wire during installation?
__________________
Model# 5883 S# 701**** (10Kw LP) w/Advanced Load Center (5449). Start-up 4-13-12
HKFever is offline   Reply With Quote
Old November 3rd, 2012   #3
GenMan
Senior Member
 
Join Date: Jan 2012
Location: Codrington , Ontario
Posts: 545
Default

same asabove , T1 has to have 120v coming to it
GenMan is offline   Reply With Quote
Old November 3rd, 2012   #4
outbackflyer
Junior Member
 
Join Date: Oct 2012
Posts: 3
Default

T1 was the problem. thanks for the info. It was hooked up but the plug between the generator junction box and the transfer switch had the pins mis -matched. T1 was in the in 4 from the transfer and pin 3 from the generator. I assume pin 4 is not used and T1 goes through Pin 3. Now that they match up the controler has power and the charger appears to be working. Thanks for the help on where to look. I now have power at T1 at the generator.
outbackflyer is offline   Reply With Quote
Old November 3rd, 2012   #5
John R
Senior Member
 
Join Date: Aug 2012
Location: Michigan, In The Thumb
Posts: 408
Default

Glad it's working, I haven't had a power outage sense I installed mine, I have run it under varying loads to get it broken in for it's first oil change.
It also exercises every week.
So far so good.


Have you run it under any loads?
__________________
John

20kW Generac 5875 air-cooled, Propane, with cold weather kit, "Minus the potentially dangerous battery heating pad." Born on 06-06-2012, Installed 07-27-2012
John R is offline   Reply With Quote
Old November 3rd, 2012   #6
outbackflyer
Junior Member
 
Join Date: Oct 2012
Posts: 3
Default

I ran it under load for testing only for about 30min. I don't have much of a load. I had the well, ejector pump and furnance all on as well as some lights and toaster oven. I had about 5A on one leg and 7A on the other. Thats about the most load it will see. I'm sure the well will cycle peaks at 10 or 12A @240V but I'm still well under my 10KW. It's all I need. Heat, water, lights and of coarse internet.

My manual says no break in required. What is the common practice for oil change and break in?
outbackflyer is offline   Reply With Quote
Old November 3rd, 2012   #7
HKFever
Senior Member
 
Join Date: Sep 2011
Location: Chesterfield VA
Posts: 610
Default

Quote:
Originally Posted by outbackflyer View Post
I ran it under load for testing only for about 30min. I don't have much of a load. I had the well, ejector pump and furnance all on as well as some lights and toaster oven. I had about 5A on one leg and 7A on the other. Thats about the most load it will see. I'm sure the well will cycle peaks at 10 or 12A @240V but I'm still well under my 10KW. It's all I need. Heat, water, lights and of coarse internet.

My manual says no break in required. What is the common practice for oil change and break in?
Run it for the eight hours called for in the manual with the non-synthetic oil the factory put in. Then change the oil and filter and follow manual guidelines. I do like breaking one in by running it thirty minutes no load, two hours 25% load, two hours 50% load, and then two hours at 75% load if possible.
__________________
Model# 5883 S# 701**** (10Kw LP) w/Advanced Load Center (5449). Start-up 4-13-12
HKFever is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:10 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
Copyright 1985-2014 Ziller Electric Inc
Ziller Electric Inc is not representing Generac Power Systems Inc